A power station delivers 100 kW of electrical power to a distant village through transmission cables with a total resistance of 5.0 Ω. In scheme A the power...

Assessment: Physics 0625 | Paper 4 Mock 01 | Theory (Extended) Subject: Physics - 0625

Question 1 Report

A power station delivers 100 kW of electrical power to a distant village through transmission cables with a total resistance of 5.0 Ω. In scheme A the power is transmitted at 1000 V. In scheme B a step-up transformer increases the voltage to 10 000 V before transmission. Fig. 44.1 shows a simplified diagram of scheme A. The student compares the power lost in the cables for each scheme, assuming ideal transformers and negligible cable resistance other than the stated 5.0 Ω. The student also calculates the percentage of power lost in the cables in each case.

diagram

(a) Calculate the current in the cables in scheme A. [2]

(b) Calculate the power lost in the cables in scheme A. [2]

(c) Calculate the current in the cables in scheme B. [1]

(d) Calculate the power lost in the cables in scheme B. [1]

(e) Explain why scheme B is more efficient for power transmission. [2]

Answer Details

Marking Scheme

  • (a) I = P / V = 100 000 / 1000 [1]; = 100 A [1]
  • (b) Plost = I²R = 100² × 5.0 [1]; = 50 000 W (50 kW) [1]
  • (c) I = 100 000 / 10 000 = 10 A [1]
  • (d) Plost = 10² × 5.0 = 500 W (0.50 kW) [1]
  • (e) Transmitting at higher voltage means lower current for the same power [1]; since Plost = I²R, a lower current greatly reduces energy wasted as heat [1]

Explanation

(a) The power station delivers 100 kW at 1000 V. Using P = IV:

\( I = \frac{P}{V} = \frac{100\,000}{1000} = 100 \text{ A} \)

(b) The power dissipated in the cable resistance is:

\( P_{lost} = I^2 R = 100^2 \times 5.0 = 50\,000 \text{ W} = 50 \text{ kW} \)

This is 50% of the total power - half the generated power is wasted as heat in the cables.

(c) In scheme B the voltage is stepped up to 10 000 V, so:

\( I = \frac{100\,000}{10\,000} = 10 \text{ A} \)

The current is 10 times smaller than in scheme A.

(d) \( P_{lost} = I^2 R = 10^2 \times 5.0 = 500 \text{ W} = 0.50 \text{ kW} \)

This is only 0.5% of the total power.

(e) For the same power delivered, increasing the transmission voltage by a factor of 10 reduces the current by a factor of 10. Since cable losses depend on I²R, reducing I by 10 reduces the power loss by a factor of 100 (from 50 kW to 0.50 kW). This is why the National Grid uses very high voltages (hundreds of kV) for long-distance transmission. Step-up transformers at the power station increase the voltage, and step-down transformers near consumers reduce it to safe levels.

Download The App On Google Playstore

Everything you need to excel in your exams

Green Bridge CBT Mobile App
Personalized AI Learning Chat Assistant
200,000+ Exam Questions Across IGCSE, JAMB, WAEC & NECO
Over 3,900 Lesson Notes
Offline Support - Learn Anytime, Anywhere
Green Bridge Timetable
Literature Summaries & Potential Questions
Track Your Performance & Progress
In-depth Explanations for Comprehensive Learning