(a) Draw a simple labelled diagram illustrating the principle of a step-down transformer and explain how it works (b) State three ways by which energy is lo...
(a) Draw a simple labelled diagram illustrating the principle of a step-down transformer and explain how it works
(b) State three ways by which energy is lost in a transformer and how they can be minimized.
(c) If a transformer is used to light a lamp rated at 60W, 220V from a 4400V a.c. supply, calculate the; (i) ratio of the number of turns of the primary coil to the secondary coil in the transformer (ii) current taken from the main circuit if the efficiency of the transforme is 95%.
(a) Step-down transformer
Labelled diagram of a step-down transformer. The primary coil has more turns than the secondary coil.
A step-down transformer has more turns in the primary coil than in the secondary coil, that is, \(N_p > N_s\). When an alternating e.m.f. is applied to the primary coil, an alternating current flows in it and produces a changing magnetic flux in the laminated soft-iron core. This changing flux links the secondary coil and induces an alternating e.m.f. in it by electromagnetic induction.
Since the induced e.m.f. is proportional to the number of turns,
\[\frac{E_s}{E_p}=\frac{N_s}{N_p}\]
As \(N_s < N_p\), \(E_s < E_p\). Hence, the output voltage is lower than the input voltage.
(b) Energy losses and their reduction
Copper loss: Heat is produced in the windings because of their resistance. This is minimized by using thick, low-resistance copper wire.
Eddy-current loss: Eddy currents are induced in the iron core and produce heating. This is minimized by laminating the core into thin insulated sheets.
Hysteresis loss: Energy is dissipated during repeated magnetisation and demagnetisation of the core. This is minimized by using soft iron or a soft magnetic material with low hysteresis loss.
(c)
Given: \(V_p=4400\text{ V}\), \(V_s=220\text{ V}\), lamp power \(P_{out}=60\text{ W}\), and efficiency \(\eta=95\%=0.95\).
Labelled diagram of a step-down transformer. The primary coil has more turns than the secondary coil.
A step-down transformer has more turns in the primary coil than in the secondary coil, that is, \(N_p > N_s\). When an alternating e.m.f. is applied to the primary coil, an alternating current flows in it and produces a changing magnetic flux in the laminated soft-iron core. This changing flux links the secondary coil and induces an alternating e.m.f. in it by electromagnetic induction.
Since the induced e.m.f. is proportional to the number of turns,
\[\frac{E_s}{E_p}=\frac{N_s}{N_p}\]
As \(N_s < N_p\), \(E_s < E_p\). Hence, the output voltage is lower than the input voltage.
(b) Energy losses and their reduction
Copper loss: Heat is produced in the windings because of their resistance. This is minimized by using thick, low-resistance copper wire.
Eddy-current loss: Eddy currents are induced in the iron core and produce heating. This is minimized by laminating the core into thin insulated sheets.
Hysteresis loss: Energy is dissipated during repeated magnetisation and demagnetisation of the core. This is minimized by using soft iron or a soft magnetic material with low hysteresis loss.
(c)
Given: \(V_p=4400\text{ V}\), \(V_s=220\text{ V}\), lamp power \(P_{out}=60\text{ W}\), and efficiency \(\eta=95\%=0.95\).